ggunn
- Austin, TX, USA
- Consulting Electrical Engineer - Photovoltaic Systems
Again, it makes no difference. It either is or it isn't. Why it is or isn't is irrelevant. When I do it it's because I can't for some reason; it's a whole lot simpler and less expensive to put the fused disco less than 10' away from the point of interconnection (which is NOT the disco) and be done with it, but if there's no room on the equipment wall for the disco I have to do something else. If I were to choose to put it somewhere else for whatever reason, I could, as long as I put current limiters at the POI.1 Can't means- you aren't allowed to *or* weren't able to.
Don't means- you do not have to, and did not.
You are free to interpret the code any way you want, and good luck with that. The way the rest of the world interprets it, however, is that the point of interconnection is where the PV conductors touch the service conductors. There is no "complication", and the fact that it appears to be such a glaring contradiction to you should suggest to you that there is maybe something wrong with your interpretation.2 And that point would be at the PV OCPD. There are PV conductors on one side, unprotected conductors on the other.
They really never touch, you have to be able to disconnect the two. There's a breaker or fused switch between them.
If the PV inverter output conductors are longer than 10' from the point of interconnection to the (fused) disco,
So there's the complication- how can something be more than 10 feet from itself?
I see the PV output connectors as connected *at* the point of interconnection *to* the fused disco, there's no way they can be 10' from it when connected to it.
If you want to tie yourself in knots over what you think the code says (when it doesn't, IMO), go ahead, but it seems pretty clear to me. I have hundreds of PV systems under my belt and I have never run into an inspector that looks at it the way you insist upon doing.
IMO you are trying to turn something simple into a Gordian Knot. It ain't that complicated, really.