The last sentence of 250.52(A)(1) prohibits the use of that portion of the interior metal water piping system that extends more than 5 ft beyond the point of entrance into the building to interconnect grounding electrodes and the grounding electrode conductor, because there are concerns over the use of nonmetallic piping or fittings causing an interruption in the interior electrical continuity of the metal water piping. The exception to 250.52(A)(1), however, permits this practice, provided there is qualified maintenance and the entire length of the water piping used as an electrode is exposed. This 5-ft limit also applies to the replacement of nongrounding receptacles with grounding-type or branch-circuit extensions in accordance with 250.130(C). See the commentary following 250.130(C) and the illustration that accompanies that commentary, Exhibit 250.49.