We are working on a repair garage, where they service small gas engines. There is a large warehouse adjacent to the repair garage, separated by a 2 HR rated wall with a door in it. I'm classifying the repair garage as Div 2 to 18" AFF.
The problem comes with that door. Does the fact that the door could be open mean that the div 2 area could extend into the warehouse? How far? NFPA 30A says that if we ventilate adjacent areas to 4 AC/HR, then they are unclassified. This is a 10,000 sft. warehouse with 20 ft ceilings. That could be a LOT of ventilation. If we don't ventilate the adjacent warehouse, is the whole thing classified because there is a 400 sft. lawnmower shop in one corner of it?
Also, if the ventilation fan can be turned off, or is on a thermostat, does it count toward the NFPA 30A required ventilation? I've been arguing it does not.
The problem comes with that door. Does the fact that the door could be open mean that the div 2 area could extend into the warehouse? How far? NFPA 30A says that if we ventilate adjacent areas to 4 AC/HR, then they are unclassified. This is a 10,000 sft. warehouse with 20 ft ceilings. That could be a LOT of ventilation. If we don't ventilate the adjacent warehouse, is the whole thing classified because there is a 400 sft. lawnmower shop in one corner of it?