I thought I was up to speed with non-incendive installations for Class I Div 2 locations but after looking at some submittal drawings today maybe I am not.
- Should a 24 volt DC power supply that is supplying power to non-incendive field devices be listed/labeled as non-incendive or suitable for use in non-incendive circuits? (I thought yes, but a quick internet search did not identify any with this 'listing')
- I am familiar with applying vendor control drawings for IS installations. Should I expect a similar control drawing non-incendive devices, with entity parameters which I then evaluate vs. the power supply parameters, similar to what would be done for an IS circuit? (I thought yes)
- The submittal drawings I am reviewing are essentially control panel drawings, identifying certain circuits as NI. The drawings are stamped "CONTROLLED DRAWING". Am I correct to be requesting 'CONTROL DRAWINGS' for the proposed NI circuits, by the device mfrs? ( I think yes)
Thanks for the head check.
- Should a 24 volt DC power supply that is supplying power to non-incendive field devices be listed/labeled as non-incendive or suitable for use in non-incendive circuits? (I thought yes, but a quick internet search did not identify any with this 'listing')
- I am familiar with applying vendor control drawings for IS installations. Should I expect a similar control drawing non-incendive devices, with entity parameters which I then evaluate vs. the power supply parameters, similar to what would be done for an IS circuit? (I thought yes)
- The submittal drawings I am reviewing are essentially control panel drawings, identifying certain circuits as NI. The drawings are stamped "CONTROLLED DRAWING". Am I correct to be requesting 'CONTROL DRAWINGS' for the proposed NI circuits, by the device mfrs? ( I think yes)