A friend called and asked some questions about a job he may do.
A residence with a remote building where the remote building has a 200 amp single phase service. The owner wants to install many, many computers in the building at 800 watts each. He is not sure how many but it may be 50 or so.
The question is if you have a load on the neutral of 1600 watts for one circuit (2 machines), and 1600 watts on the neutral for the other phase, then is load on the neutral 1600 watts. If I think about the service as a multiwire branch circuit then the neutral load would be "zero" but I don't think it works that way.
Secondly, once the neutral is calculated and the non-linear loads are more than 50% then how do we size that neutral ?
Thirdly, do we need to even worry about this on single phase since the code mentions harmonics for a 3 phase wye and not single phase.
A residence with a remote building where the remote building has a 200 amp single phase service. The owner wants to install many, many computers in the building at 800 watts each. He is not sure how many but it may be 50 or so.
The question is if you have a load on the neutral of 1600 watts for one circuit (2 machines), and 1600 watts on the neutral for the other phase, then is load on the neutral 1600 watts. If I think about the service as a multiwire branch circuit then the neutral load would be "zero" but I don't think it works that way.