The AHJ finally got back to me and said to use the higher of the motor's nameplate FLA or the interpolated FLA from 1996 NEC table 430.150.

For a 35HP, 480V, 3? motor the interpolated FLA is 46A. The nameplate FLAs on both motors are around 42A so I'm using 46A for each.