Nongrounding receptacle replacement NEC vs. IEBC

Status
Not open for further replies.

olc

Senior Member
To replace a non-grounding type receptacle, the International Existing Building Code, says (if no equipment grounding conductor) "....shall be permitted to be grounded to any accessible point on the grounding electrode system....".
This is not one of the options listed in NEC Article 406.

1. A viable option if your state uses the IEBC?

2. Is a metal box and armored cable part of the grounding electrode system?
 
250.130(C)

(C) Nongrounding Receptacle Replacement or Branch Circuit
Extensions. The equipment grounding conductor of a
grounding-type receptacle or a branch-circuit extension shall
be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) An equipment grounding conductor that is part of
another branch circuit that originates from the enclosure
where the branch circuit for the receptacle or branch
circuit originates
(5) For grounded systems, the grounded service conductor
within the service equipment enclosure
(6) For ungrounded systems, the grounding terminal bar
within the service equipment enclosure
 
250.130(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following: (1) Any accessible point on the grounding electrode system as described in 250.50 (2) Any accessible point on the grounding electrode conductor (3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates (4) An equipment grounding conductor that is part of another branch circuit that originates from the enclosure where the branch circuit for the receptacle or branch circuit originates (5) For grounded systems, the grounded service conductor within the service equipment enclosure (6) For ungrounded systems, the grounding terminal bar within the service equipment enclosure Informational Note: See 406.4(D) for the use of a ground-fault circuit-interrupting type of receptacle.

Right from reading the 460 articles on circuits.. which falls right into the IEBC codes...
 
Thanks for the replies.
I was not aware of 250.130(C).

Practically speaking - typically when a non-grounding receptacle is replaced, it is in an older house or similar situation where it is not convenient to run a ground wire anywhere.
so:
1. Is there a easy way to make this ground connection that is not occurring to me?
2. Do you usually just use one of the methods in 406.4(D)?
 
Thanks for the replies.
I was not aware of 250.130(C).
To me, the most versatile part of 250.130(C) is 250.130(C)(4) which permits using a local Equipment Grounding Conductor. In that case, your OP question #2 comes back into play if the metal box and armored cable are connected as an equipment grounding conductor or a grounding means.

Practically speaking - typically when a non-grounding receptacle is replaced, it is in an older house or similar situation where it is not convenient to run a ground wire anywhere.
so:
1. Is there a easy way to make this ground connection that is not occurring to me?
I humbly suggest, Yes, and that is to NOT add the ground connection as per 406.4(D)(2).

2. Do you usually just use one of the methods in 406.4(D)?
NO. And that is because I generally have to use More Than One of the parts of 406.4 as per the second sentence of the rule:
2017 NEC
406.4 General Installation Requirements.
. . . . General installation requirements shall be in accordance with 406.4(A) through (F).
Satisfying a requirement of part of 406.4(D) ("one of the methods") does not relieve me from all the rest of 406.4 if it applies to the situation of a specific installation.

So, practically speaking, when working under the 406.4 as written in the 2014 and 2017 NEC, today, in your OP scenario, the most efficient solution is to thread together 406.4(D)(4) with 406.4(D)(5) and 406.4(D)(2)(b) when using a single device that is a GFCI / AFCI Outlet Branch Circuit receptacle device that includes Tamper Resistance. This device is available from several manufacturers and is tested and evaluated to work without a connection to an EGC. In many existing installations, the nongrounding type receptacle replacement will be a direct swap out with no collateral damage, and will take a short fraction of an hour.
 