I was hoping to find some clarity on the proper installation for a particular transmitter in a Class 1 Division 2 location.
The transmitter in question is a MicroMotion 2700R12DBAEZZZ. This transmitter requires a power source (which will be 24vdc) and intrinsically safe outputs. It is not connected to a process source (therefore no process seals required).
After looking at the datasheet (page 13 link) it appears that the device "provides nonincendive sensor outputs for use in Class I, Div. 2, Groups A, B, C, and D..." or intrinsically safe outputs for Class 1 Div 1 locations.
After reading NEC 501 until I have a headache, I am still a little unclear on how this device needs to be installed.
Field Wiring:
My thinking is that this device would be best categorized as a nonincendive device as defined by 500.2. As such it should be wired per 501.13 (B)(3) - Nonincendive field wiring. According to this article, I can use any of the wiring methods permitted for unclassified areas as long as it is consistent with the control drawing.
Are control drawings always this difficult to find? I have called the manufacturer and they said "All you should need to do for a class 1 div 2 is install a conduit seal and you are nonincendive." You are joking right?
Frustrated with this response and thinking that I was missing some key piece of understanding I accepted this explanation (temporarily). Because this didn't sit straight with me, I did another google search and found an installation manual that shows hazardous area mA output wiring (page 90 link).
Does this mean that I still need an ISB for the mA output even if I use nonincendive field wiring?
What about the power supply to the transmitter?
I couldn't find anything remotely close to a control drawing for that.
Lastly, once I get all that sorted out, do I need a conduit seal at the transmitter? My interpretation of 501.15(B) is that no conduit seal is required at the transmitter; only need one when leaving the Class1 Div.2 location.
Thanks for all the help.
The transmitter in question is a MicroMotion 2700R12DBAEZZZ. This transmitter requires a power source (which will be 24vdc) and intrinsically safe outputs. It is not connected to a process source (therefore no process seals required).
After looking at the datasheet (page 13 link) it appears that the device "provides nonincendive sensor outputs for use in Class I, Div. 2, Groups A, B, C, and D..." or intrinsically safe outputs for Class 1 Div 1 locations.
After reading NEC 501 until I have a headache, I am still a little unclear on how this device needs to be installed.
Field Wiring:
My thinking is that this device would be best categorized as a nonincendive device as defined by 500.2. As such it should be wired per 501.13 (B)(3) - Nonincendive field wiring. According to this article, I can use any of the wiring methods permitted for unclassified areas as long as it is consistent with the control drawing.
Are control drawings always this difficult to find? I have called the manufacturer and they said "All you should need to do for a class 1 div 2 is install a conduit seal and you are nonincendive." You are joking right?
Frustrated with this response and thinking that I was missing some key piece of understanding I accepted this explanation (temporarily). Because this didn't sit straight with me, I did another google search and found an installation manual that shows hazardous area mA output wiring (page 90 link).
Does this mean that I still need an ISB for the mA output even if I use nonincendive field wiring?
What about the power supply to the transmitter?
I couldn't find anything remotely close to a control drawing for that.
Lastly, once I get all that sorted out, do I need a conduit seal at the transmitter? My interpretation of 501.15(B) is that no conduit seal is required at the transmitter; only need one when leaving the Class1 Div.2 location.
Thanks for all the help.