Ok, I have been trying to do an interesting to me calculation of a home with a granny apartment in it. It is based upon four floors including the basement. But, I have been getting myself confused when trying to compare with or without the apartment, so, someone correct me or show me the correct codes at least: Here it is..lol...
Apartment:
19 feet by 50 feet 3va 2850 Va
3 small appliance circuits 4500
stove 8000
no washer
no dryer
no heating or cooling
No other appliances
total usage: 15350
first 8000
15350 – 8000 = 7350 * 0.40 = 2940
/240 45.6 50 amps
no stove__ 7350 amps/240v 30.6 amps
Whole house calc with apartment:
4 floors including basement and apartment
33 by 50 times 4 floors times 3Va = 19800
11 small appliance circuits over three floors 16500
garbage disposal 1176
2 ranges 16000
2 laundry 3000
0 dryers 0
2 dishwashers 2400
3 waterpumps 3528
total usage 62404
first 8000
62404-8000=54404 *0.40 = 21761 =29761
= 124 amps
if take out both stoves: 46404 so 23361 = 97.35 amps.
If I take out the circuits for the apartment… I get
47054 Va = 23621 = 98.42 amps. Or 85 amps without stove...
So somehow I get less amps with apartment than without apartment. What am I doing wrong?
Apartment is one range probably gas but...set for 8000 electric just in case
3 small appliance circuits
no washer or dryer
no extras.
Am I messing up somewhere???
Apartment:
19 feet by 50 feet 3va 2850 Va
3 small appliance circuits 4500
stove 8000
no washer
no dryer
no heating or cooling
No other appliances
total usage: 15350
first 8000
15350 – 8000 = 7350 * 0.40 = 2940
/240 45.6 50 amps
no stove__ 7350 amps/240v 30.6 amps
Whole house calc with apartment:
4 floors including basement and apartment
33 by 50 times 4 floors times 3Va = 19800
11 small appliance circuits over three floors 16500
garbage disposal 1176
2 ranges 16000
2 laundry 3000
0 dryers 0
2 dishwashers 2400
3 waterpumps 3528
total usage 62404
first 8000
62404-8000=54404 *0.40 = 21761 =29761
= 124 amps
if take out both stoves: 46404 so 23361 = 97.35 amps.
If I take out the circuits for the apartment… I get
47054 Va = 23621 = 98.42 amps. Or 85 amps without stove...
So somehow I get less amps with apartment than without apartment. What am I doing wrong?
Apartment is one range probably gas but...set for 8000 electric just in case
3 small appliance circuits
no washer or dryer
no extras.
Am I messing up somewhere???