A while back I started a thread on failed Power Factor Correction capacitors and VFDs. I would refer to it if I could find it.
This is a seasonal operation so full scale testing for harmonics at this time could result in a $10,000 utility bill for a non productive month. Total connected HP is 1425. VFD hp is 69 HP. Less then 5% of the total. Of that 69 HP, only 3 3hp motors do not have line and load reactors. From my reading I believe 10% to 15% of total HP was the magic number where concern may/should begin.
We ran a short test with the 60 HP of VFDs and a 100 HP fan with PFC. We used a Fluke 43B and several Fluke true RMS meters. As expected the THD with just the drives running was up to 57%. THD dropped to 3.4% after the 100 HP was started with only the 5th harmonic showing on graph. Only .2 amp increase in capacitor amperage was noted. I expected more.
The plant does not suffer from low voltage even at max load. 3-300 KVA xfmrs with less than 25000 sca according to utility. Considerably less than I expected. 2.4% impedance 480/277 with no neutral load.
The plant PFC is manually controlled via fused disconnect at the start/end of day. Could I use an educated guess that maybe it was cycled on-off-on before it could discharge competely or am I still in denial?
This is a seasonal operation so full scale testing for harmonics at this time could result in a $10,000 utility bill for a non productive month. Total connected HP is 1425. VFD hp is 69 HP. Less then 5% of the total. Of that 69 HP, only 3 3hp motors do not have line and load reactors. From my reading I believe 10% to 15% of total HP was the magic number where concern may/should begin.
We ran a short test with the 60 HP of VFDs and a 100 HP fan with PFC. We used a Fluke 43B and several Fluke true RMS meters. As expected the THD with just the drives running was up to 57%. THD dropped to 3.4% after the 100 HP was started with only the 5th harmonic showing on graph. Only .2 amp increase in capacitor amperage was noted. I expected more.
The plant does not suffer from low voltage even at max load. 3-300 KVA xfmrs with less than 25000 sca according to utility. Considerably less than I expected. 2.4% impedance 480/277 with no neutral load.
The plant PFC is manually controlled via fused disconnect at the start/end of day. Could I use an educated guess that maybe it was cycled on-off-on before it could discharge competely or am I still in denial?