Aleman
- Southern Ca, USA
What we did and this was ok'd by our engineer. This is a industrial control panel, fed from 480V/300A.
We installed 3 14 awg wires into the lugs at top of panel disconnect, along with the feeders. The lugs are not specified for multiple cables. The 14awg is sandwiched behind the
main cables which I believe are size 500, maybe 350. The 14awg's are yellow and run about 1-1/2 feet into a circuit breaker that protects a 24DC supply. I don't believe this to
be exactly ok per NEC multiple conductors in a lug not marked, but on the other hand I believe we have a good connection. This would be also under the tap rule correct?
But ok other than multiple wires on the lug. The yellow wires are colored per UL508A and are marked accordingly.
This is a dual control panel set, one is DC control only and the main has motor drives, contactors etc. The idea is to be able to turn off the 480V to the motor drives and leave power
on the control side.
Any opinions?
Any opinions?