-38 Log #573 NEC-P01
Final Action: Reject
(100.Lighting Outlet)
__________________________________________________ ___________
Submitter:
Alan H. Nadon, City of Elkhart, IN
Recommendation:
Revise as follows:
Lighting Outlet. An outlet having intended for the direct connection of a
lampholder, a luminaire (lighting fixture), or a pendant cord terminating in a
lampholder, that is directly connected .
Substantiation:
Intent cannot be determined during an inspection. A junction
box with a blank cover, even one containing switched conductors, does not
provide the illumination needed for persons to move about safely thus
preventing accidents.
Panel Meeting Action: Reject
70-22
Report on Proposals A2007
? Copyright, NFPA NFPA 70
Panel Statement:
The proposed definition would require a luminaire
wherever a lighting outlet is installed. Code rules dictate where lighting is
required. CMP-1 refers the submitter to the panel action and statement on
Proposal 1-39.
Number Eligible to Vote: 12
Ballot Results:
Affirmative: 12
I had the opportunity to run this by the other men working in my department. Two of which are master code officials. The other is an electrical inspector with over twenty years experience all of which are certified electrical inspectors. They believe you cannot read into the panel?s action what is not there.
They ask that you consider the recommendation as stated. There is no distinction in this recommendation between required lighting outlets and optional lighting outlets. They fill changing the definition that a lamp holder that is directly connected will limit the installer?s choice on non required lighting outlets. The example they give is a lighting outlet in a closet is installed and does not meet the required separation from the storage area, they believe since this is not a required lighting outlet as code rules dictate the owner should be left with the option of blanking off this non required lighting outlet. Changing the definition of lighting outlet to require a lamp holder or fixture connected would remove the option of not installing non-required lighting fixtures if you roughed in a box that could be defined as a lighting outlet by present definition.
Secondly they believe to much is being read into the panel statement They would ask since this is a NEC panel, would not the code rules that the panel is referring in their statement be the NEC, if not , wouldn?t they have been more clear as to what codes they where referring to. They would highlight the fact that CMP did not say building code rules dictate where lighting is required. They went on further to say, after rechecking the language in the residential building code, the language that would require lighting outlets in these area?s is in the electrical section of the residential building code, and the NEC is the referenced standard to that section of the residential building code. (the point being that there is no stronger language in the international residential building code, except for stairways, and a couple of other area's, the inspectors in my department believe the language in the NEC is such that would require illumination ( required lighting outlets ) )
They also believe that 210.70 ( C ) is requiring as a min standard a lighting fixture with a self contained switch and the second sentence goes on to say that a wall controlled lighting outlet ( fixture), that would be more then meeting the min. code, would be an acceptable way of meeting the lighting requirements this area. Someone in our group ask how could a pull chain fixture both meet the requirement that an outlet be at the equipment and the control being at the point of entry. We then discussed that the size of the room would be a consideration if you ever been in an old timers basement pull strings where commonly extended to a point of control.
I am not going to argue this point any more it?s just something for you guys to consider. We have not been able to conclude as of yet that lighting fixture are not required in the areas that the code requires lighting outlets.
Edited this sentence was left out
(the point being that there is no stronger language in the international residential building code, except for stairways, and a couple of other area's, the inspectors in my department believe the language in the NEC is such that would require illumination ( required lighting outlets ) )
Final Action: Reject
(100.Lighting Outlet)
__________________________________________________ ___________
Submitter:
Alan H. Nadon, City of Elkhart, IN
Recommendation:
Revise as follows:
Lighting Outlet. An outlet having intended for the direct connection of a
lampholder, a luminaire (lighting fixture), or a pendant cord terminating in a
lampholder, that is directly connected .
Substantiation:
Intent cannot be determined during an inspection. A junction
box with a blank cover, even one containing switched conductors, does not
provide the illumination needed for persons to move about safely thus
preventing accidents.
Panel Meeting Action: Reject
70-22
Report on Proposals A2007
? Copyright, NFPA NFPA 70
Panel Statement:
The proposed definition would require a luminaire
wherever a lighting outlet is installed. Code rules dictate where lighting is
required. CMP-1 refers the submitter to the panel action and statement on
Proposal 1-39.
Number Eligible to Vote: 12
Ballot Results:
Affirmative: 12
I had the opportunity to run this by the other men working in my department. Two of which are master code officials. The other is an electrical inspector with over twenty years experience all of which are certified electrical inspectors. They believe you cannot read into the panel?s action what is not there.
They ask that you consider the recommendation as stated. There is no distinction in this recommendation between required lighting outlets and optional lighting outlets. They fill changing the definition that a lamp holder that is directly connected will limit the installer?s choice on non required lighting outlets. The example they give is a lighting outlet in a closet is installed and does not meet the required separation from the storage area, they believe since this is not a required lighting outlet as code rules dictate the owner should be left with the option of blanking off this non required lighting outlet. Changing the definition of lighting outlet to require a lamp holder or fixture connected would remove the option of not installing non-required lighting fixtures if you roughed in a box that could be defined as a lighting outlet by present definition.
Secondly they believe to much is being read into the panel statement They would ask since this is a NEC panel, would not the code rules that the panel is referring in their statement be the NEC, if not , wouldn?t they have been more clear as to what codes they where referring to. They would highlight the fact that CMP did not say building code rules dictate where lighting is required. They went on further to say, after rechecking the language in the residential building code, the language that would require lighting outlets in these area?s is in the electrical section of the residential building code, and the NEC is the referenced standard to that section of the residential building code. (the point being that there is no stronger language in the international residential building code, except for stairways, and a couple of other area's, the inspectors in my department believe the language in the NEC is such that would require illumination ( required lighting outlets ) )
They also believe that 210.70 ( C ) is requiring as a min standard a lighting fixture with a self contained switch and the second sentence goes on to say that a wall controlled lighting outlet ( fixture), that would be more then meeting the min. code, would be an acceptable way of meeting the lighting requirements this area. Someone in our group ask how could a pull chain fixture both meet the requirement that an outlet be at the equipment and the control being at the point of entry. We then discussed that the size of the room would be a consideration if you ever been in an old timers basement pull strings where commonly extended to a point of control.
I am not going to argue this point any more it?s just something for you guys to consider. We have not been able to conclude as of yet that lighting fixture are not required in the areas that the code requires lighting outlets.
Edited this sentence was left out
(the point being that there is no stronger language in the international residential building code, except for stairways, and a couple of other area's, the inspectors in my department believe the language in the NEC is such that would require illumination ( required lighting outlets ) )