david said:NEC requires a switched controlled ceiling outlet in these areas min standard.
david said:The problem is the NEC language used in 210.70 is flowed. Their no way that the NEC wrote a requirement into a safety a life safety code as an exercise with out an end.
david said:I said Tom what do you mean, he said there have been plenty of times that I have installed lighting fixtures and you did not require me to first install a box you allowed me to take the wire straight to the fixture and with a smile he said so you let me finish the house with out the NEC required lighting outlet.
Now all is left is to find out what constitutes an ?outlet.?Lighting Outlet. An outlet intended for the direct connection of a lampholder, a luminaire (lighting fixture), or a pendant cord terminating in a lampholder.
I didn?t see in either definition where a box is required in order to fit the definition of ?Outlet? or ?Lighting Outlet.?Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
I would say that the NEC required lighting outlet was the wiring compartment of the fixture, where the premises wiring ended.david said:...and with a smile he said so you let me finish the house with out the NEC required lighting outlet.
georgestolz said:I would say that the NEC required lighting outlet was the wiring compartment of the fixture, where the premises wiring ended.
IMO, the luminaire can be used as both an outlet box and a luminaire, much the same way they can be both a luminaire and a raceway per 410.31.![]()
iwire said:David as is often the case Roger was able to get right down to the main point.
You are happy to listen to anyone that agrees with you and refuse to believe the CMP members themselves with the excuse being 'these CMP members did not actually right the rule'.
The fact is we don't need to hear from any CMP members to apply the rule as written and the words written do not include luminaire.
georgestolz said:I would say that the NEC required lighting outlet was the wiring compartment of the fixture, where the premises wiring ended.
IMO, the luminaire can be used as both an outlet box and a luminaire, much the same way they can be both a luminaire and a raceway per 410.31.![]()
david said:Once again Bob you bring personal insults since you only have a snapshot of who I am and you seem to be forming your opinion based on a single discussion we are having not the whole picture, I will give little merit to your opinion of me.
Some ones character is always open for attacks because it is something you can not defend only time will prove it.
david said:My building department would like me to add to this post that they are not saying CMP-2 is wrong they want me to make it clear that they are paying particular attention to the statement CMP-2 made in this ROP
I am of the opinion that only the outlet for a fixture is required and the fixture is not required to be installed.david said:Panel Statement:
The proposed definition would require a luminaire
wherever a lighting outlet is installed. Code rules dictate where lighting is
required. CMP-1 refers the submitter to the panel action and statement on
Proposal 1-39.
?Wherever a lighting outlet is installed? is what my building department believes is key in this statement. They believe as I do this would be to inclusive and would include Non-required lighting outlets as well as required lighting outlets.
We were wondering if instead of changing the definition of lighting outlet the proposal would have requested a new definition for Required lighting outlets perhaps he would have got a more favorable response from CMP- 2
My building department would also like to know if you guys have a statement from CMP that would clearly state that illumination is not being required by the NEC when the NEC asked for required lighting outlets.
It is clear that you are thinking that the requirement 210.70(A)(3) means that the lighting fixture is where the switch is located where this section says,? at least one lighting outlet containing a switch?.david said:McGraw Hills National Electrical Code Handbook 25th adition
Page 180
? Part ( C ) of 210.70 requires that either a lighting outlet containing a switch ?such as the familiar pull-chain porcelain lampholder ?or the wall ?switched controlled lighting outlet must be provided in attics or underfloor spaces housing heating.?
Can we agree thet 210.70 ( C) " a lighting outlet contain a switch" is a fixture that the Code is requiring as a min to meet the lighting requirements in the first sentence in 210.70 ( C )