kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Probably was a 240 volt heater at some time and someone not knowing exactly what they were doing removed and re used the line for a receptacle - and somehow interconnected with another existing circuit. When GFCI isn't tripped, you should have at very least a line to neutral fault and trip at least one of the breakers, and likely the GFCI at the same time.Very strange because there is no dining room heater. There is also no living room heater but there is a 2 pole breaker labeled such with a 12-2 UF cable connected to it������
I had a house with a fuse panel one time that had a fuse that apparently had a short circuit/ground fault because whenever you put a new fuse in it instantly blew. Was somewhat newer house then most with fuse panels, but still built in 50's or early 60's. Thing was even with this blown fuse there didn't seem to be anything in the house that didn't work.
finally found that circuit was mistakenly tied to another circuit in a box somewhere supplied by the other 120 volt line, so any time you put in a fuse you were closing a 240 volt line to line fault.