Jesse7623
Senior Member
- Location
- eastern Mass
is the neutral considered a current carrying conductor in a multi wire?? I thought it is but one of my guys says its not.
is the neutral considered a current carrying conductor in a multi wire?? I thought it is but one of my guys says its not.
310.15(B)(4) Neutral Conductor.
(a) A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(2)(a).
(b) In a 3-wire circuit consisting of two phase conductors and the neutral conductor of a 4-wire, 3-phase, wye-connected system, a common conductor carries approximately the same current as the line-to-neutral load currents of the other conductors and shall be counted when applying the provisions of 310.15(B)(2)(a).
(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral conductor shall therefore be considered a current-carrying conductor.
In a multiwire branch the neutral is considered a current carrying conductor unless the circuit is balanced at all times
What says how much unbalance it has to carry to make it a ccc
It doesn't matter how much unbalanced load there is. Unless you have more than 50% nonlinear load, the neutral is not a current carrying conductor. The derating is based on heat from the I^2R losses in the conductors. With a 120/240 volt multiwire branch circuit, the worst case for heat is either with one ungrounded conductor fully loaded or with both fully loaded. In both cases there are two conductors carrying the full amount of current and the other carrying none.What says how much unbalance it has to carry to make it a ccc
now what about a standard 2 wire circuit? do you count the neutral then?
That's as long as all supply phases present are included. As mentioned above, the neutral of a 3-wire circuit derived from a 4-wire Y system would be a CCC.It doesn't matter how much unbalanced load there is.