Have a VAV replacement project going in a school environment. The new VAV have electric heating elements in them. We are experiencing an issue where the main breaker (3000Amp insulated case breaker with a Siemens ETU776 trip unit) is tripping at random.
The electrical distribution is pretty straight forward, Siemens Distribution Board feeds smaller branch panel around the facility. They only adjustable trip unit is the Main Breaker. All other breaker are just inverse time thermal breakers.
Is it possible that a faulty heater inside VAV can trip the main? All VAVs are fed from 20Amp /277V circuits. Heaters are 3-5KW. This is the first cold day of the year, so I'm guessing this is the issue. Is there a quick way to check each VAV? We have 30-40 new ones so it would take some time.
The only other thing I can think of is it is coming in from the Utility side. If you guys can think of any other reasons for nuisance tripping a 3000A main I'm all ears.
The electrical distribution is pretty straight forward, Siemens Distribution Board feeds smaller branch panel around the facility. They only adjustable trip unit is the Main Breaker. All other breaker are just inverse time thermal breakers.
Is it possible that a faulty heater inside VAV can trip the main? All VAVs are fed from 20Amp /277V circuits. Heaters are 3-5KW. This is the first cold day of the year, so I'm guessing this is the issue. Is there a quick way to check each VAV? We have 30-40 new ones so it would take some time.