Nuisance tripping of GFI

Status
Not open for further replies.
Hello and good morning
i would like to know if anyone has had past experience with GFIs tripping when it shares a neutral wire between 2 circuits feeding 2 GFIS.
Example circuits 7 and 9 feeding separate devices and sharing the same neutral

Thank you
Eric
 
Clarify for me, please.
Circuit 7 & 9 using standard breakers (not GFCI, not AFCI, and not Dual function), sharing a neutral with a GFCI receptacle on each circuit ??
 
Did you hook the neutral to the line side when passing thru to the second receptacle? The neutral of a multiwire branch circuit cannot be connected to the load.