Can a single service with a single service disconnect have more than one bond jumper?
L lfloyd Member Nov 7, 2013 #1 Can a single service with a single service disconnect have more than one bond jumper?
iwire Moderator Staff member Location Massachusetts Nov 7, 2013 #2 lfloyd said: Can a single service with a single service disconnect have more than one bond jumper? Click to expand... Yes. Consider bonding a meter socket followed by the MBJ in the service disconnect enclosure.
lfloyd said: Can a single service with a single service disconnect have more than one bond jumper? Click to expand... Yes. Consider bonding a meter socket followed by the MBJ in the service disconnect enclosure.
L lfloyd Member Nov 7, 2013 #3 If this is done, are both bond jumper required to be sized per 250.66 or the UL standard for the equipment? Can one be a #12 for a 100amp service?
If this is done, are both bond jumper required to be sized per 250.66 or the UL standard for the equipment? Can one be a #12 for a 100amp service?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Nov 8, 2013 #4 lfloyd said: Can one be a #12 for a 100amp service? Click to expand... No it cannot. 250.28