one of the guys on the job are installing 42- #10 current carrying conductors in a 2" conduit.
I checked into it and according to table 310.15 (B 3 a) which is the adjustment factors table, it reads that above 40 current carrying conductors must be reduced by 35% of its original ampicity.
According to table 310.15 ( B 16 ) a #10 THHN has a max ampicity of 40a, after reducing to 35% the #10 now has a ampicity of only 14A. These conductors are slated to be terminated on 20A circuit breakers.
I certainly see his installation as a violation.
Am I correct on this or am I misunderstanding the tables and the adjustment methods.
I checked into it and according to table 310.15 (B 3 a) which is the adjustment factors table, it reads that above 40 current carrying conductors must be reduced by 35% of its original ampicity.
According to table 310.15 ( B 16 ) a #10 THHN has a max ampicity of 40a, after reducing to 35% the #10 now has a ampicity of only 14A. These conductors are slated to be terminated on 20A circuit breakers.
I certainly see his installation as a violation.
Am I correct on this or am I misunderstanding the tables and the adjustment methods.