kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
the pull box is a absolute mess. According to your calculations you are saying that all those wires could fit into a 8x8x8 pull box which is 512 ci. I did not even look at the table but I find it hard to believe that the NEC is saying
that 210 conductors ( 84 0f them being #10s) can enter and splice to one another and this leaves a safe work men like installation. And if the NEC is stating this to be true than they are horribly mistaken as to the space required to accomplish this task.
I think 18x18 has sufficient room, but certainly would hate to work in there if you are going to "wire nut" all 210 of those.
I would be mounting some terminal blocks in there instead of wire nutting everything. Maybe double tier din rail style, grounded and ungrounded of each circuit on each block.