Tom.Margillo
Member
If someone can explain derateing to me I would appreciate it. What is the maximum number of#12awg or #10awg current carrying conductor allowed in a 2 1/2" conduit?
Tom.Margillo said:If someone can explain derateing to me I would appreciate it. What is the maximum number of#12awg or #10awg current carrying conductor allowed in a 2 1/2" conduit?
finhead said:I think Tallgirl has it exactly right, but permit me to extend the question with an example.
Fifty 12 AWG THW current carrying conductors are installed in a raceway. After applying adjustment factors the ampacity of each conductor is 8.75 amps. (25 x 0.35)
Now, the next higher standard OCPD is a 10 amp fuse. If the building has only circuit breakers, would 15 amp circuit breakers be acceptable?
infinity said:They make 10 amp circuit breakers. What kind of load would you put on a 10 amp circuit?
finhead said:I think Tallgirl has it exactly right, but permit me to extend the question with an example.
Fifty 12 AWG THW current carrying conductors are installed in a raceway. After applying adjustment factors the ampacity of each conductor is 8.75 amps. (25 x 0.35)
Now, the next higher standard OCPD is a 10 amp fuse. If the building has only circuit breakers, would 15 amp circuit breakers be acceptable?
paul said:I'm going to load that puppy up with 176 THHN #12's and call 'em control wires. However, it's up to y'all to pull and terminate 'em.![]()
roger said:I agree with Trevor, then after adjusting these conductors and using 10 amp breakers you would not have to guard to bedroom circuits with AFCI's.
Roger
Jim W in Tampa said:Use # 14 and get even more in it LOL.You make the head and i will put our tugger on it.
Jim W in Tampa said:Nice try but they require 15 or 20 amp receptacles.
finhead said:My question is also a thought problem. Section 240.6 does not recognize 10 amp circuit breakers as a standard OCPD.
But you can't use that 8.75 amp wire on a 10 amp breaker to feed receptacle outlets. 240.4(B)(1)I agree with Trevor, then after adjusting these conductors and using 10 amp breakers you would not have to guard to bedroom circuits with AFCI's.
don_resqcapt19 said:Roger,
But you can't use that 8.75 amp wire on a 10 amp breaker to feed receptacle outlets. 240.4(B)(1)
Don