As illustrated in Exhibit 220.3, the 180-volt-ampere load is applied to single and multiple receptacles mounted on a single yoke or strap, and a 360-volt-ampere load is applied to each receptacle that consists of four receptacles. These are considered receptacle outlets, in accordance with 220.3(B)(9). The receptacle outlets are not the lighting outlets installed for general illumination or the small-appliance branch circuits, as indicated in 220.3(B)(10). The receptacle load for outlets for general illumination in one- and two-family and multifamily dwellings and in guest rooms of hotels and motels is included in Table 220.3(A). The load requirement for the small-appliance branch circuits is 1500 volt-amperes per circuit, as described in 220.16(A).
Exhibit 220.3 The 180-volt-ampere load requirement of 220.3(B)(9) as applied to single- and multiple-receptacle outlets on single straps and the 360-volt-ampere load applied to each receptacle that consists of four receptacles.
Note in Exhibit 220.3 that the last outlet of the top circuit consists of two duplex receptacles on separate straps. That outlet is calculated at 360 volt-amperes because each duplex receptacle is on one yolk. The multiple receptacle supplied from the bottom circuit that comprises four or more receptacles is calculated at 90 volt-amperes per receptacle (4 ? 90 VA = 360 VA). For example, single-strap and multiple-receptacle devices are calculated as follows:
Device Computed Load
Duplex receptacle 180 VA
Triplex receptacle 180 VA
Double duplex receptacle 360 VA (180 ? 2)
Quad or four-plex-type receptacle 360 VA (90 ? 4)
A load of 180 volt-amperes is not required to be considered for outlets supplying recessed lighting fixtures, lighting outlets for general illumination, and small-appliance branch circuits. To apply the 180-volt-ampere requirement in those cases would be unrealistic, because it would unnecessarily restrict the number of lighting or receptacle outlets on branch circuits in dwelling units. See the note below Table 220.3(A) that references 220.3(B)(10). This note indicates that the 180-volt-ampere requirement does not apply to most receptacle outlets in dwellings.
In Exhibit 220.4, the maximum number of outlets permitted on 15- and 20-ampere branch circuits is 10 and 13 outlets, respectively. This restriction does not apply to outlets connected to general lighting or small-appliance branch circuits in dwelling units.
Exhibit 220.4 Maximum number of outlets permitted on 15- and 20-ampere branch circuits.