Design/Calculate or Just Plain USE
Design/Calculate or Just Plain USE
For some sadistic reason I gotta point out a few more facts:
Fact is 215-2(A)(1) ?Feeder conductors shall have an ampacity not less than required to supply the load as CALCULATED in parts II, III, and IV of Article 220?
Fact is 220-10 ?The calculated load of a feeder or service shall not be less than the sum of the loads on the branch circuits supplied, as determined by Part II of this article? which includes 220-14(I) ?receptacle outlets shall be CALCULATED at not less than 180 volt-amperes?
Fact is Annex D3, Noncontinuous Loads, Receptacle Load, 80 receptacles at 180 VA = 14,400 VA. This is a contributing calculation used to determine ?Minimum Size Feeder (or Service) Overcurrent Protection?
Fact is 225-5 ?The ampacity of outdoor branch-circuitry and feeder conductors shall be in accordance with 310-15 based on loads as determined under 220-10 and Part III of Article 220?
Fact is 230-23(A) ?Conductors shall have sufficient ampacity to carry the current for the load as CALCULATED in accordance with Article 220?
And
Fact is 210-11 ?Branch circuits?shall be provided to supply the loads CALCULATED in accordance with 220-10? This is simply telling us to use the 180 VA found in Article 220 just like it does for feeders and services.
The above facts do reveal some commons: branch circuits, feeders, outside branch circuits & feeders, and services all use CALCULATIONS that include 180 VA for receptacles to determine ampacity and overcurrent protection and they all refer to Article 220 for this calculation.
Design/Calculate or Just Plain USE
For some sadistic reason I gotta point out a few more facts:
Fact is 215-2(A)(1) ?Feeder conductors shall have an ampacity not less than required to supply the load as CALCULATED in parts II, III, and IV of Article 220?
Fact is 220-10 ?The calculated load of a feeder or service shall not be less than the sum of the loads on the branch circuits supplied, as determined by Part II of this article? which includes 220-14(I) ?receptacle outlets shall be CALCULATED at not less than 180 volt-amperes?
Fact is Annex D3, Noncontinuous Loads, Receptacle Load, 80 receptacles at 180 VA = 14,400 VA. This is a contributing calculation used to determine ?Minimum Size Feeder (or Service) Overcurrent Protection?
Fact is 225-5 ?The ampacity of outdoor branch-circuitry and feeder conductors shall be in accordance with 310-15 based on loads as determined under 220-10 and Part III of Article 220?
Fact is 230-23(A) ?Conductors shall have sufficient ampacity to carry the current for the load as CALCULATED in accordance with Article 220?
And
Fact is 210-11 ?Branch circuits?shall be provided to supply the loads CALCULATED in accordance with 220-10? This is simply telling us to use the 180 VA found in Article 220 just like it does for feeders and services.
The above facts do reveal some commons: branch circuits, feeders, outside branch circuits & feeders, and services all use CALCULATIONS that include 180 VA for receptacles to determine ampacity and overcurrent protection and they all refer to Article 220 for this calculation.