This is yet another one of those topics where unconventional wisdom and outside the box thinking can only end in tears IMO.

220.3(B)(10) excludes many dwelling outlets from "further calculation"

If your inspector is of the very conventional thinking that circuits should be sized for the load, and calculated at 180VA per yoke other than what is clearly excluded - you're gonna have a bad time kids....:D :roll:


So whats next - we ignore all of 220 and put in what-ever sized service we want, or size the building for the service we install instead?
 
Last edited:
I am not sure but let me being blunt for a min but i did read somewhere one state did make a admendment to the code change one state stated that 15 amp circuits no more than 10 repectales while 20 amp circuits no more than 13 repectales.

IMO it pretty much paralleled with the Cananda Electrical code [ i know some of you will scream at me but i have a feeling there will be more change along the way but i dont have all the answer ATM ]

Merci, Marc
 
ItsHot said:
All of 'em!

Ummm - no.

You can put as many as you want on a single circuit, but you can't put all of them.

You have to have two SABCs that cannot serve other outlets, you have to have a laundry circuit, you have at least one bathroom circuit, etc.,etc.
 