That's 220.3(B)(9) in the 2002 and it doesn't apply to dwellings.By bh:
Per NEC 220.14(I) each receptacle on one yoke shall be calculated at not less than 180va.
I would never treat a receptacle circuit as "continuous," regardless of what is plugged in, if by that you mean that you would multiply the 180 VA times 125%. Our design and installation efforts are based on 180 VA, not on any potential future use of the receptacle.Originally posted by roger:Bh, why would you consider a receptacle circuit continuous unless you knew specifically what the use was?
why do you think this is silly?Originally posted by allenwayne:
silly yes legal same answer.
And when was the last NEC cycle this was required?ahhh the good old days points limits on a circuit.How did that go away?