gregorsc

Member
How many duplex receptacles will the NEC allow on a 20a 120v circuit in a doctors office ? DO YOU APPLY THE CONTINUOUS DUTY 125% RULE?
 
Re: Number of receptacles

Unless you know the circuit will be loaded more than 16 amps for more than 179 min 59 sec at a time, it is not necessary to calculate for continous duty.

See 220.3(B)(9) for how many receptacles on a circuit.

Roger
 
Re: Number of receptacles

Better check your local rules. Parma, Ohio only allows 10 outlets of any kind on a 20 amp circuit. If all of the outlets are LED exit signs then tough. They also ban 15 amp wiring.

For that matter, not using 15 amp wiring simplifies my situation anyways. Only need to remember 1 set of box fills, 1 set of Sctchlok(R) fills, less fragmentation of inventory.
 
Re: Number of receptacles

" Parma, Ohio only allows 10 outlets of any kind on a 20 amp circuit. If all of the outlets are LED exit signs then tough. They also ban 15 amp wiring."

Is this a written code change, or a myth generated and perpetuated in the field?
 
Re: Number of receptacles

Originally posted by jimwalker:
Sure would complicate wiring up layins in a large building.
Good point, using compact florescent fixtures at 277 volt we might have 60 or 80 fixtures on a circuit. :D
 