shespuzzling
Member
- Location
- new york
Hi,
Trying to reconcile NEC 2008 210.21(B)(2) with 220.14(I), specifically Exhibit 220.4 which is in the 2008 Handbook. See attached for the two excerpts.
I had previously convinced myself that the maximum number of convenience outlets that could be on a single 20A branch circuit is 13. (180VA per outlet * 13 outlets = 2340VA, which is under 20A*120V=2400VA). This was under the assumption that the NEC prescribed load for convenience outlets already takes into account continuous vs non-continuous loading. Exhibit 220.4 also shows 13 outlets on a 20A branch circuit.
Now reading 210.21(B)(2) I'm not so sure. Has anybody else noticed this apparent contradiction? What's the actual max # of outlets on a 20A circuit?

Trying to reconcile NEC 2008 210.21(B)(2) with 220.14(I), specifically Exhibit 220.4 which is in the 2008 Handbook. See attached for the two excerpts.
I had previously convinced myself that the maximum number of convenience outlets that could be on a single 20A branch circuit is 13. (180VA per outlet * 13 outlets = 2340VA, which is under 20A*120V=2400VA). This was under the assumption that the NEC prescribed load for convenience outlets already takes into account continuous vs non-continuous loading. Exhibit 220.4 also shows 13 outlets on a 20A branch circuit.
Now reading 210.21(B)(2) I'm not so sure. Has anybody else noticed this apparent contradiction? What's the actual max # of outlets on a 20A circuit?
