Number of receptacles on 20 amp branch circuit
Number of receptacles on 20 amp branch circuit
Hi, I am new to posting on the forum, but browse it frequently. One thing I didn't see anyone mention in the first couple of pages is that the code book is not a design manual. It is for minimum acceptable standards to protect property and safeguard life. Sorry, I don't have my code book with me at the moment... , so that is paraphrasing. That being said, the only limit to the number of receptacles on a 20 amp branch circuit, in a house for example, is common sense!
As other members stated earlier, the 180 va/receptacle is for load calculation purposes only.
It was common practice once upon a time to have one gfci protected circuit feed all outside receptacles as well as bathroom receptacles, garage, basement...
Was that practical for a well designed electrical system? No, not even close; however, it was perfectly legal. How many times did those circuits trip because there were 2 hairdryers going at the same time?
We cannot control what Clark Griswald plugs in to his receptacles, but we can apply some common sense when we lay-out our electrical circuits and try to keep him from burning down his house
Number of receptacles on 20 amp branch circuit
Hi, I am new to posting on the forum, but browse it frequently. One thing I didn't see anyone mention in the first couple of pages is that the code book is not a design manual. It is for minimum acceptable standards to protect property and safeguard life. Sorry, I don't have my code book with me at the moment... , so that is paraphrasing. That being said, the only limit to the number of receptacles on a 20 amp branch circuit, in a house for example, is common sense!
As other members stated earlier, the 180 va/receptacle is for load calculation purposes only.
It was common practice once upon a time to have one gfci protected circuit feed all outside receptacles as well as bathroom receptacles, garage, basement...
Was that practical for a well designed electrical system? No, not even close; however, it was perfectly legal. How many times did those circuits trip because there were 2 hairdryers going at the same time?
We cannot control what Clark Griswald plugs in to his receptacles, but we can apply some common sense when we lay-out our electrical circuits and try to keep him from burning down his house