I have a 1200 A 1ph Service on a ag site, then it branches out to 4 200 a panels one in each building. I am wondering if I can add a second panel in each building.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Would each new panel have a feeder separate from the original? If so I would say no. Look at 225.30 which limits the number of feeders to a building to one, unless you can meet one of the special conditions outlined in 225.30(A).
 

69spark

Member
the original feeder, was installed several years ago as a "main feed", now we are upgrading the service and establishing the service at the gen set site. All the panels are now going to be sub panels. i would like to run to 4 wire sets to each building and have to panels. the way it is sounding i will have to talk to my inspector.

thanks for the input
 