We followed up an EC that had put, IIRC, six all in the same conduit. Motors were always burning up but they were in a very high ambient and not knowing better, we just replaced motors as they died.When you run multiple cables in a conduit, all of the surrounding magnetic fields are expanding and collapsing at the same frequency, cancelling each other out, so there are negligible mutual induction effects. But when you involve VFDs, their outputs are NOT at the same frequencies, so they do NOT cancel. It gets real ugly real fast, resulting in motor winding damage, conductor insulation breakdown and possible transistor damage. So the answer to your question as to how many circuit, the answer is 1, unless you use fully shielded BFD cable for each individual motor circuit, with the shielded grounded at both ends.
That’s one approach. I had a gravel pit that had run 16 2HP drive circuits in one 4” conduit out to the trap feeders at the bottom of the piles, with breakouts for each one. They decided, after I pointed out the problem, that it was cheaper to keep replacing the motors than to dig new trenches to redo it correctly or to pull all the wires out and replace them with VFD cables. It only had to last until the mine ran out, so likely less than 10 years. I couldn’t argue with the logic…We followed up an EC that had put, IIRC, six all in the same conduit. Motors were always burning up but they were in a very high ambient and not knowing better, we just replaced motors as they died.
Now that I think about it, it was one drive feeding those motors. Each with separate overload.That’s one approach. I had a gravel pit that had run 16 2HP drive circuits in one 4” conduit out to the trap feeders at the bottom of the piles, with breakouts for each one. They decided, after I pointed out the problem, that it was cheaper to keep replacing the motors than to dig new trenches to redo it correctly or to pull all the wires out and replace them with VFD cables. It only had to last until the mine ran out, so likely less than 10 years. I couldn’t argue with the logic…
Now that I think about it, it was one drive feeding those motors. Each with separate overload.