I have now, been told so many different methods, and have read so many different parts of the forum, so I just better ask this,
In a load center, panel board, or safety switch, can (2) two wires be connected to the load of a single circuit breaker
In the forum, I have read that it is determined if the lug is permitted for more that one wire, and that this is a parallel circuit
However I have many electricians quoting parts of the code restricting this method, and I have not found any part telling me (2) two wires are not permitted to a breaker.
We have this application: the customer has a 20A 2P CB off it, they run a hot from both legs to a (4) four pole lighting contactor
Can someone tell me if it is not permitted and the location in the code restricting it,
Or if it is permitted and the location in the code allowing it,
Thanks
Robert
In a load center, panel board, or safety switch, can (2) two wires be connected to the load of a single circuit breaker
In the forum, I have read that it is determined if the lug is permitted for more that one wire, and that this is a parallel circuit
However I have many electricians quoting parts of the code restricting this method, and I have not found any part telling me (2) two wires are not permitted to a breaker.
We have this application: the customer has a 20A 2P CB off it, they run a hot from both legs to a (4) four pole lighting contactor
Can someone tell me if it is not permitted and the location in the code restricting it,
Or if it is permitted and the location in the code allowing it,
Thanks
Robert