NYC electrical code 408.60(E)(4) and (5)

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
408.60(E)(4) and (5) talks about sizing the through (main) bus and section bus. The code section can be found here:

https://www.nyc.gov/assets/buildings/pdf/ll39of2011_electrical_code.pdf

How exactly do I perform this calculation? is this calculation my responsibility or the manufacturer's responsibility?

For example if I have (6)-600 amp disconnect switches fed by a through bus, does this mean the minimum rating of the switchboard needs to be:

6 x 600 amps x 70% = 2520 amp rated switchboard required
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I think that this would fall on the switchboard manufacturer and wouldn't be the concern of the designer.
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
I think that this would fall on the switchboard manufacturer and wouldn't be the concern of the designer.
Here's what I also don't understand, when we for example tell the manufacturer that we want a 3000 amp switchboard,

is the 3000 amps the through bus rating? How does the manufacturer make the calculation based on the parameters we provide them?
 