where in the nec would i find a code on how close can an electrical panel be located near a gas meter ????
The basic rule is not in the NEC; it is in Section 5.7.2.3 of NFPA 54, the NATIONAL FUEL GAS CODE:where in the nec would i find a code on how close can an electrical panel be located near a gas meter ????
-and let me also echo Volta's welcome.Gas meters shall be located at least 3 ft (0.9 m) from sources of ignition.
Here's a link to the Con ed spec. Its on page 33.
For indoor locations it's 36"
http://coned.com/es/specs/gas/Section VI.pdf