stevenj120volts
Member
- Location
- Tommy7rings**
- Occupation
- Master Electrician
In a video demonstration I made i put a load if 67amps in a panel all 67 amps was on one hot and one neutral in the feeder. Then on a branch circuit fed form that panel i made a connection between the neutral and equipment ground at the receptacle. This cause 22 amps of objectionable current to flow thru the connection. Do think that is a sign or other problems or is that what should happen when you make a connection between neutral and ground on the load side of the service disconnecting means ?