Im in a commercial building with a slightly older 208v 3 phase system. outside the building there is a 200a main breaker that feeds a sub panel inside the building. the sub panel has a #6 ground wire going from the neutral lug in the main disconnect box directly to the main neutral bus of the sub panel. The neutral bus is not bonded to the chassis. I'm assuming this was once legal, and as such is "grandfathered." i can measure about 2-5a of current on the ground wire when there is about 25-30a flowing through the neutral. is this an objectionable current i should concern myself with? is it worth my while to install a ground bus to the chassis of the box and bring the sub up to current standards? all of the existing circuits are currently only using conduit as ground conductor and if i end up adding circuits i will most definitely be including a grounding conductor in my wire runs. that being said, i would much rather attach to a ground bus than the neutral bus of a sub panel.
what does the NEC say about adding circuits to an existing panel that was wired as such?
what does the NEC say about adding circuits to an existing panel that was wired as such?