What would you fellas reccamend to switch on a small exhaust fan in a commercial bathroom a straight 120v switching relay or a low voltage sensor with a separate relay. What brands and model's are you guys typically using looking for something celling mointed

Sent from my SM-G965U using Tapatalk
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Whatever you chose you need a relay or contacts to switch the fan, not solid state. There should be occupancy sensors that have dry contacts that will work for you.

-Hal
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
I think all RIBs have a horsepower rating, just different amps, contact voltages and coil voltages. I'm a big fan of Functional Devices' product line. Standard RIB U1C should do the trick. I believe you can have either 120-volt or 10-30 volt AC or DC coil signal. The U1C has a rating of 1/3 HP @ 120 volts.
 