Panel Statement: The permission to use 230.40, Exception No. 1 has been in the NEC for the past 60 years in one form or another without a requirement for location plaques to be installed at each disconnect location. Where there are more than six disconnect locations, the proposal would require all supply characteristics to be clearly described using graphics or text or both on a plaque. Locating this graphic/text plaque on the building in a readily accessible location that is acceptable to the authority having jurisdiction, usable for any location identification, and that is as near as practicable to the point of attachment or service entrance entry into the building would be extremely difficult on all but the smallest buildings.
...