Elect117
- California
- Engineer E.E. P.E.
It is a common issue on the utility side. High resistance return makes the fault look like load but the fault location with available energy is still enough to hurt or cause fire.
It typically requires zones of protection and monitoring of voltage sags or phase shifts to catch.
The return path is really how you are going to catch it. Whether that is a wire type EGC, conduit, neutral, bonded metal piping, etc.
I don't know if what Jim is saying relieves me of the the possibility of the long line impedance still being capable of harm at the fault location since it will be trying to get on it's return path.
Like a PVC run with wire type EGC vs RMC for 2000'. Does the pipe being a high impedance return create a difference in potential and capable of shock?
I guess it is two issues at once. The wire at the fault end might arc but not be destroyed but could the fault location (if somewhere between load and breaker) have enough available energy / difference in potential to shock someone touching the RMC? And should the breaker be able to protect against that.
I agree with the point that the breaker will protect the wire but is that enough for the NEC?