Plenty of times. The Generac/Guardian service-rated ATS's are examples.RUWired said:Has anyone ever used an auto transfer switch with a main breaker in it.
Thats what asco is saying, It needs to be in a seperate compartment prior to the ats.They don't make this with it built in.So then if a main needs to be installed prior to an ats, then i would'nt call it service rated.LarryFine said:The service disconnect must be either ahead of, or part of, the ATS. The service OCPD may be ahead of, part of, or after but adjacent to, the ATS.
RUWired said:Has anyone ever used an auto transfer switch with a main breaker in it.I dont think theres enough room to actually put a breaker.
RUWired said:So then if a main needs to be installed prior to an ats, then i would'nt call it service rated.
LarryFine said:Or, to put it another way, it can't be considered service-rated.
RUWired said:Plenty of room but does it have a main in it?
chris kennedy said:It sure does and an 800A switch also. I'll PM you a pic of the guts tomorrow.