We're replacing an old 15 kVA Ferrups (ferroresonant UPS system) with a shiny new dual-conversion online UPS. The Ferrups output feeds a pair of main-lug breaker panels about 25 feet away. There is no other OCPD on the output. The input is protected by a fused disconnect. As I understand it, this installation was deemed acceptable under 450-3a because the output of the Ferrups is a transformer and the unit is located in a supervised location. I've got my reservations, since the Ferrups can continue to produce output even if the input is disconnected -- that's the whole idea! OTOH, by its very nature a UPS is current-limited when on inverter.
Does this configuration comply with NEC?
If this config IS acceptable, is it also acceptable for my new (non-transformer output) online UPS, or do I need to put in an additional OCPD?
Thanks!
D.