tallgirl
Senior Member
- Location
- Glendale, WI
- Occupation
- Controls Systems firmware engineer
We may be coming at this from opposite sides.I was responding to a post where Jon stipulated a fault that would draw more than 12 times the inverter rating. No listed inverter is going to maintain the set output voltage at 12 times its current rating.
Perhaps pvnoob's situation with commercial is different, but in the resi work I do I'm near certain that any fault that isn't too much to shut down the inverters is in the thermal (not magnetic) range of any OCPDs. In other words, longer clearing times no matter if the source is utility or microgrid. It's faults that are over the inverters ability to keep outputting voltage where the behavior will be different.
Since inverters aren't going to have the available fault current in the magnetic portion of the curve, perhaps it's time to re-evaluate the delay period in the thermal part of the curve. In just math terms, that's how I'd express what I'm trying to say.