Good afternoon,

To size an overcurrent protection device for a pump @ Rated voltage 208V, Rated Current 11.9A, and Staring current 76.8A. Should the starting current be used for sizing OCPD or the Rated current. I thought are if you use the rated current, the device would trip every time you start the pump. Also to account for the load (wattage) on the panel schedule, which current (Staring or Rated )should be used.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IIn most cases You should size the GFSC protection from Tables. See 430.6, Tables 430.247-251 & 430.52
Overload protection should be size from the nameplate. See 430.32
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Motor overcurrent protective device are based on percentage of the value from T.430.248, .249, .250. That percentage is determined by T. 450.52

1668543589792.png
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are you asking about motor overload or overcurrent protection? There are two different sets of answers in this thread.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
There are two threads going on this, reply to this one.............
 