I suppose my understanding of the Duty Cycle is what confuses me. I thought 100% meant you could use the welder for the full 10 minutes as opposed to 30% which is only 3 minutes in a 10 minute period. But that seems to go against the currents listed. Lower Duty Cycle + higher amp draw
To pile onto what was already said, 100% duty cycle can be non-stop welding, so everything has to be continuous rated for heat soak. 30% duty cycle is non-continuous, so you need to be able to handle the peak draw without a nuisance trip. A time delay 25A fuse is going to handle something in the neighborhood of 50A for 3 minutes, a normal operating fuse may be closer to 25A at that time. You have to consider each component is affected in each scenario and go with the worst of each.