OCPD Size for Harmonic Filter

Status
Not open for further replies.
Location
IN, USA
We have a 1400kVAr switched passive harmonic filter fed from a 2500A circuit breaker recently installed. The rated capacitor current for the unit is 1680A = (1000 X 1400kVAr/(1.73 X 480V)). According to the NEC Article 460 and the mfg. installation manual, conductor size to feed the unit should be a minimum of 135% X 1680A. The installation guide says a fused disconnect should be sized at least 165% of the rated capacitor current of 1680A, but says nothing about sizing a circuit breaker and the NEC says the OCPD should be as low as practicable. The wire was sized correctly for a 2500A breaker. The breaker keeps tripping after about 2 hours on what appears to be an overload. The highest current measured on the load side of the breaker was 1920A (notably about 15% higher than nameplate FLA) which is still less than 80% of the breaker rating. The electrician tried disabling 200kVAr (about 240A), but still the breaker tripped.

Question: Is a 2500A molded case, 80% rated CB with digital trip unit too small for 1400kVAr? Since the breaker also tripped with only 1200kVAr engaged, could the breaker have an internal problem??

Thanks for your help!!
 
Yes. The breaker may have an internal problem. Replacing the trip unit of the breaker by another one may solve the problem.
 
Are there settings on the breaker? Have you checked them? Does the breaker tell you what function caused the trip?
 