Re: ocpd
Step One:
Calculate the load. Not having the original problem at my disposal, I will presume that you did that part right. I interpret the original posting as saying that the calculate load is 920 amps. I must then further presume (as templdl has already pointed out) that this result correctly accounts for continuous and non-continuous loads.
Step Two:
Find a set of conductors that can take every bit of that 920 amps. You can get a bigger conductor, but this is not the time to ?round down.?
Step Three:
Find an OCPD that is higher than 920, but no higher than the ampacity of your selected conductors.
Step Four:
At this point, you discover THE TRAP! If in Step Two you picked, for example a set of 4 conductors of size 4/0, you have an ampacity of 920 amps. You must then take the next lower size of OCPD, which is 800 amps. This will not carry the calculated load, and would cause you to fail the test question.
The Solution:
You want to be able to select a 1000 amp OCPD. This means that the conductors must be sized for at least 1000 amps. Lacking any other information on design constraints, I would select a set of 4 conductors sized 250 MCM.
I think that this portion of the original posting is the cause of a bit of confusion here. Several members have already pointed out the error in this statement. The error comes from trying to round, up or down, from the calculated load.Originally posted by tower:. . . after calculating the amps on a feeder that came out to 920 amps, to size the ocpd you would round down to the next smallest size.
Step One:
Calculate the load. Not having the original problem at my disposal, I will presume that you did that part right. I interpret the original posting as saying that the calculate load is 920 amps. I must then further presume (as templdl has already pointed out) that this result correctly accounts for continuous and non-continuous loads.
Step Two:
Find a set of conductors that can take every bit of that 920 amps. You can get a bigger conductor, but this is not the time to ?round down.?
Step Three:
Find an OCPD that is higher than 920, but no higher than the ampacity of your selected conductors.
Step Four:
At this point, you discover THE TRAP! If in Step Two you picked, for example a set of 4 conductors of size 4/0, you have an ampacity of 920 amps. You must then take the next lower size of OCPD, which is 800 amps. This will not carry the calculated load, and would cause you to fail the test question.
The Solution:
You want to be able to select a 1000 amp OCPD. This means that the conductors must be sized for at least 1000 amps. Lacking any other information on design constraints, I would select a set of 4 conductors sized 250 MCM.