al hildenbrand
- Minnesota
- Electrical Contractor, Electrical Consultant, Electrical Engineer
Thanks for this, George. I've managed to miss the ring circuit debate until now.Consider the attached picture.
Assuming the circuit breaker handles are tied together, could you legally use a pair of 12-2 NM cables to go to different points in a kitchen, and then combine them back together to come into, say, an island with a single 12-3 NM cable?
While the neutral current between the breakers and #3 junction box are parallel, the conductor between j-box #1 and its breaker is not a paralleled conductor with the neutral conductor between j-box #2 and its breaker. IMO this doesnot fall within the purview of 2011 NEC 310.10(H)