winnie
- Springfield, MA, USA
- Electric motor research
As others have said, I strongly suspect capacitive coupling...with a couple of red flags.
'Phantom voltage' is seen where AC flows through the parasitic capacitance formed between two wires lay beside each other. There insulation is in fine shape and the wires are perfectly usable. When you measure with a 'high impedance' meter (a volt meter that draws very little current) then you see a significant voltage; but when you measure with any sort of load the voltage vanishes.
Phantom voltage is very real, and some of the industrial electricians here, working at 277V with long runs will tell you that you can get a shock from a disconnected wire simply sitting in a conduit with live wires.
What gives me pause simply dismissing this as phantom voltage is the magnitude of the effect you are seeing. Running a phone charger requires more than the microamps that I would expect from capacitive coupling in romex at 120V.
I wonder if you are mixing up two different 'measurements':
A) phantom voltage measured in the wires when disconnected, which is giving you your meter values.
B) current leaking through the switch, measured by the loads getting partial power. Are these by any chance 'lighted' switches?
-Jon
-Jon