If this is "normal" then why have I never experienced this amount before.
I don't believe we're saying "this is normal", rather, that the voltage readings have errors caused by the meters themselves. You asked "Anyone heard of this before?" And we answered, "yes" and "we've DONE this before."
As to why you've never experienced this, I simply can't say.
Dan, the high input impedance, of digital volt meters you report having used, is introducing significant error in the readings you are reporting to us. . . how much, that is yet to be determined, if you wish. A low input impedance measurement uses enough energy to make the reading that any charge is dissipated in the wiring being measured and, as a result, a reading is made that is sustainable under load.
Based upon your original trouble report from the occupants about the "Christmas tree lights were on dim", it sounds almost certain that there is something really wrong. The only thing that would change my judgement is the nameplate specs of the "Christmas tree lights." I hope you can learn the specs and share them with us. If the Christmas tree lights are a fractional Watt load (not likely, but unknown to me at this moment), then it is entirely possible that alone is the source of the "trouble."
Better yet, I hope you are able to actually use the occupant's Christmas tree lights as a test load in a trouble shooting mode that I suggest back in Post #28.