I'm pricing a job that will have 28 boatlifts. There will be a power center with breakers (2 per power center) for the boatlift between 2 slips (for a total of 14 power centers).
What I want to do is run a feeder looping from power center to power center, then the branch breaker in the power center will provide the overcurrent protection for the boatlift motors. Each lift should have (2) 1-HP or less motors.
I want to put 7 power centers on each feeder (for a total of 14 boatlifts per feeder). I want to use #4 type W cable which gives me an ampacity on the feeder of 115 amps (table 400.5(B)). If you add all the motor ampacity together you get 224-amps (28 motors * 8-amps) not adding in 25% of 2 motors for the starting current.
The chances of multiple boatlifts being operated simultaneously are small. The chances of 4 lifts being operated at the same time are very very small. When these lifts operate, at most, they will run for 5-7 minutes (probably more like 3-4 minutes).
Now to the question. Does the code allow/prevent me from loading these feeders this much?
What I want to do is run a feeder looping from power center to power center, then the branch breaker in the power center will provide the overcurrent protection for the boatlift motors. Each lift should have (2) 1-HP or less motors.
I want to put 7 power centers on each feeder (for a total of 14 boatlifts per feeder). I want to use #4 type W cable which gives me an ampacity on the feeder of 115 amps (table 400.5(B)). If you add all the motor ampacity together you get 224-amps (28 motors * 8-amps) not adding in 25% of 2 motors for the starting current.
The chances of multiple boatlifts being operated simultaneously are small. The chances of 4 lifts being operated at the same time are very very small. When these lifts operate, at most, they will run for 5-7 minutes (probably more like 3-4 minutes).
Now to the question. Does the code allow/prevent me from loading these feeders this much?