I have movable office partitions that come with a 8 wire 4 circuit whip. I want dedicated neutrals for the 3 circuits feeding the partitions and all ungrounded conductors must deenergize per NEC 605.7. Is it ok for 1 ground wire to be used to serve the 3 circuits feeding the partitions, or do I need a ground wire for each circuit?